Generator transfer panel

Thread view: 
Enable EMail Alerts  Start New Thread
Thread rating: 
Bill - 19 Aug 2008 02:00 GMT
What is a good rule of thumb for the length of wire?
I read where you should not exceed 25' from the 'Transfer Panel" to your
"Main panel", and 25' from the Generator to your "Transfer panel".

I can understand 25' from transfer to the main, because the number of wires,
but I have a need to run 50' from my 7550w generator to the transfer panel.
(10/3wG).
John Grabowski - 19 Aug 2008 12:47 GMT
> What is a good rule of thumb for the length of wire?
> I read where you should not exceed 25' from the 'Transfer Panel" to your
[quoted text clipped - 3 lines]
> wires, but I have a need to run 50' from my 7550w generator to the
> transfer panel. (10/3wG).

Another contractor that I know usually places the generator as far away as
possible from the house to keep the noise away.  Check with the
manufacturer.
PeterD - 19 Aug 2008 16:26 GMT
>What is a good rule of thumb for the length of wire?
>I read where you should not exceed 25' from the 'Transfer Panel" to your
>"Main panel", and 25' from the Generator to your "Transfer panel".

Other than building codes? (if applicable) AFAIK, there is no
restriction in the distance from the power source (generator) and the
transfer panel. The transfer panel location may have restrictions
however. Ask your local building inspector, he'll be the final say
regardless. Any local licensed electrican should also be able to set
this up in a proper manner-just ask around before you hire someone.

>I can understand 25' from transfer to the main, because the number of wires,
>but I have a need to run 50' from my 7550w generator to the transfer panel.
>(10/3wG).

What is (10/3wG)

Are you saying you want to connect a 7500 watt power source with 10
AWG wire? If that is the case, you are nuts... You could run it with 4
AWG without too much trouble, but never in a million years would you
get satisfactory service with 10 AWG wire, even for shorter distances.
Now if (10/3wG) is not what size wire you are planning to use...
ransley - 20 Aug 2008 17:48 GMT
> What is a good rule of thumb for the length of wire?
> I read where you should not exceed 25' from the 'Transfer Panel" to your
[quoted text clipped - 3 lines]
> but I have a need to run 50' from my 7550w generator to the transfer panel.
> (10/3wG).

My 7500 has maybe 6 or 8 ga outside, research it you might need 4 ga
at that length.
Twice Retired - 20 Aug 2008 20:07 GMT
On Aug 18, 8:00 pm, "Bill" <barg...@bellsouth.net> wrote:
> What is a good rule of thumb for the length of wire?
> I read where you should not exceed 25' from the 'Transfer Panel" to your
[quoted text clipped - 5 lines]
> panel.
> (10/3wG).

My 7500 has maybe 6 or 8 ga outside, research it you might need 4 ga
at that length.

I have an 8KW @ 110 feet and wire size is #6.
Bill - 20 Aug 2008 22:39 GMT
I like the idea of 50' of #6.
I Think 4 is over kill for 50'. Not allot of current draw here.

> On Aug 18, 8:00 pm, "Bill" <barg...@bellsouth.net> wrote:
>> What is a good rule of thumb for the length of wire?
[quoted text clipped - 11 lines]
>
> I have an 8KW @ 110 feet and wire size is #6.
Craig M - 23 Aug 2008 18:11 GMT
I think the reason for shorter runs from main to transfer panel is that from
gen to transfer is 240 v, so amps is less, from transfer to main its going
to be 120 v, so amps will go up, and most panels are wired with 12 ga wire,
just keep in mind, overall its the toal watts that count, and running from
gen to transfer panel, I would go over kill on the line there, because its
all going through that line.
> What is a good rule of thumb for the length of wire?
> I read where you should not exceed 25' from the 'Transfer Panel" to your
[quoted text clipped - 3 lines]
> wires, but I have a need to run 50' from my 7550w generator to the
> transfer panel. (10/3wG).
Dottie - 26 Aug 2008 00:27 GMT
> I think the reason for shorter runs from main to transfer panel is that from
> gen to transfer is 240 v, so amps is less, from transfer to main its going
[quoted text clipped - 9 lines]
> > wires, but I have a need to run 50' from my 7550w generator to the
> > transfer panel. (10/3wG).

The people I know who have transfer panels have them located almost
side by side with the circuit breaker box.  One of these people is an
electrician...  they just use real long extension cords to connect to
the generators.  The generators are placed outside the garage - some
in the driveway and one is outside the side of the garage.  The
installer cut a hole in the concrete large enough for a cord to go
through and then put a removable metal plate over it to cover when not
in use.  This way the owner could anchor the generator to a piece of
metal embedded in concrete in the ground so the generator would not be
stolen.
 