> Good photos....not the worst work I've seen but it ain't any where near
> the best.
>
> Did the SE do a site visit?
He did, but before the old wall came down. He hasn't seen the new
work, unless he's read his email recently.
> Looks like the floor plywood is taking the load at the header rather
> than the joists...one of the joists looks like it has a joist hanger
> but not the others?
The work is in progress.. only a few of the joists have hangers so far.
There are still temporary support walls in place on both sides of the
header. As far as the plywood taking the load (necessary due to
extensive wiring), this is supposed to be addressed with shims.
(hopefully that's ok, the SE said it should be)
> All that notching isn't great, if your GC does that sort of work....I'm
> now concerned about the built-up post....how did he interface it with
> the basement floor? So it can wick moisture & rot?
I think this was done well, see photo here (
http://i18.tinypic.com/4h86tfk.jpg ).
> Let's see what your SE says......I would suggest slapping two more
> 2x6's so you can get some header bearing under the area beyond the
> notches.
That's kind of what I was thinking.
> As for the joists...how about a piece of OSB sistered to the LVL (full
> depth) & add some joist hangers...might want to jam a temporary supoprt
> (2x4, floor to josit) under the joist while installing the
> hangers.....use nails longer than the normal joist hanger nails so you
> can get into the LVL
If that's structurally sound, then great... we can all get out of this
without too much trouble. The temporary wall is still in place so this
should not be too difficult.
> but really you should get the "fix" from your SE (& your GC should pay,
> if there are any charges)
>
> cheers
> Bob
Thanks for your help.
- S
Bobk207 - 29 Dec 2006 16:11 GMT
> > Good photos....not the worst work I've seen but it ain't any where near
> > the best.
[quoted text clipped - 46 lines]
>
> - S
S-
Ooops! I missed the support wall in the first photo...that make me
feel a lot better as does the post base.detail.....I take back 1/2 of
my comments :)
Now the only thing troubling me is the notched beam end
Depending on the load & what your SE says, more support under the beam
end might be needed.
Per Bob M's comments......the 3/8 to 1/2 joist end gap will be taken up
by the joist hangers and an OSB fillers trip is overkill but if the GC
is going to shim them & the work will not be visible then I guess you
can forget about it.
cheers
Bob