Floating a 3/4" Solid Hardwood Floor Over Above Grade Concrete?
|
|
Thread rating:  |
lefebvre@iwavesolutions.com - 19 Dec 2006 20:06 GMT I am interested in floating a solid hardwood plank floor (3/4" x 3"). Has anyone successfully done this? I am leary of glue down application onto the above grade cement slab. Here in Hawaii we have alot of moister in the air and I feel that allowing the the floor to shrink and grow and generally allowed to roam is a better option than locking it down which then could lead to buckling and other nasty things. Plus wood floors are supposed to give and take underfoot and not fee like contrete.
I have successful tried this in a small room in the house for testing and all went well and it has been over a year with no issues to date. I left 1/2" gap all round the room for expansion space. Now, I want to do the main living room which is a lager space and higher traffic area. What are your thoughts, ideas, recomendations, and concerns?
-Marc
dpb - 19 Dec 2006 20:57 GMT > I am interested in floating a solid hardwood plank floor (3/4" x 3"). > Has anyone successfully done this? I am leary of glue down application > onto the above grade cement slab. ... ...
> What are your thoughts, ideas, recomendations, ... Go straight to the horse's mouth, so to speak (National Organization of Floor Manufacturers) installation guidelines/instructions has all you need to know...
You can install wood flooring above or on grade concrete if slab is prepared and drains properly and proper moisture-barrier protection/provisions are followed.
https://www.nofma.org/Portals/0/Publications/NOFMA%20Installing%20Hardwood%20Flo ors.pdf
resrfglc - 19 Dec 2006 21:25 GMT INSTALLATIONS OVER A CONCRETE SLAB. Hardwood flooring can be installed successfully over a slab which is on-grade or above grade. Below-grade installations are not recommended. The slab must be constructed properly (dry and flat with a trowel finish). Watch out for water. New concrete is heavy with moisture, an inherent enemy of wood. Proper on-grade slab construction requires a vapor retarder such as 6 mil polyethylene film between the gravel fill and the slab. While this prevents moisture entry through the slab, this membrane also retards curing of the slab. So test for dryness, even if the slab has been in place over two years. Slabs younger than 60-days are generally too wet for flooring installation.
>I am interested in floating a solid hardwood plank floor (3/4" x 3"). > Has anyone successfully done this? I am leary of glue down application [quoted text clipped - 12 lines] > > -Marc Swingman - 19 Dec 2006 21:52 GMT <lefebvre@iwavesolutions.com> wrote in message
> I am interested in floating a solid hardwood plank floor (3/4" x 3"). > Has anyone successfully done this? Absolutely ... around here (Gulf Coast) hardwood floors are routinely installed on concrete slab foundations thusly:
The concrete floor is first sealed with a layer of hot tar.
1" - 1 1/2" "screeds" (ripped SYP 2 x 4's are commonly used) are then placed on top of the tar about 12", or less, apart.
The hardwood floor planks are then laid perpendicular to the screeds and nailed to them, leaving approximately 1/2" - 3/4" room for expansion along all walls.
The expansion gap is then covered partially by the baseboard and completely by the shoe molding.
Hardwood floors done in this manner on concrete slabs generally survive better in this climate than hardwood floors laid on the subfloor of a crawlspace foundation.
 Signature www.e-woodshop.net Last update: 12/19/06
lefebvre@iwavesolutions.com - 20 Dec 2006 03:27 GMT Thanks for the tips. It seems that many installation provisions recomended boil down to a nail down type installation, either over a plywood subfloor over concrete, or the use of screeds. However, what about my orignal idea of actually "floating" it?
Here is what I did on my test room:
1) My house is over 5 years old and the concrete is dry as its ever gonna be. It tested well. 2) I laid out a poly/foam vapor barrier over the entire space, with 12" overlaps and is taped using 3m blue tape. 3) I glued each plank of the 3/4" solid wood flooring to its neighbor via the tung and groove. 4) left a 1/2" space around the entire perimeter of the room.
Thats it. The floor is floating much like an engineered product would be installed, but is a solid 3/4" plank floor (3" wide). The room has been going good for over a year now. Has seen all the seasons.
Is this a crazy idea?
> <lefebvre@iwavesolutions.com> wrote in message > [quoted text clipped - 19 lines] > better in this climate than hardwood floors laid on the subfloor of a > crawlspace foundation. resrfglc - 20 Dec 2006 04:59 GMT "using 3m blue tape"
Hey, you have demonstrated that it works in your location. What can we possibly add absent such personal experience.
Assume new installation is also at or above grade as well (below grade installs over concrete are the iffy installations).
Not sure 3M Blue Masking tape would be my choice for the vapor barrier as opposed to the tape sold for use with Tyvex House Wrap or similar.
I'm wrestling with a below-grade concrete basement floor I want to serve as my workshop and would love it if your approach mightwork. But the moisture would create MOLD big time if the wood pulled off the one basement wall is any indication.
From what I've found, there's little one can do with a below-grade cement basement floor and medical advice is "don't spend time standing on concrete!"
Catcha-22
> Thanks for the tips. It seems that many installation provisions > recomended boil down to a nail down type installation, either over a [quoted text clipped - 43 lines] >> better in this climate than hardwood floors laid on the subfloor of a >> crawlspace foundation. dpb - 20 Dec 2006 14:57 GMT > "using 3m blue tape" > > Hey, you have demonstrated that it works in your location. What can we > possibly add absent such personal experience. ...
Well, he's demonstrated it for _one_ year for a flooring product that traditionally installed could be expected to last multiple lifetimes. Not exactly a conclusive test. :)
> I'm wrestling with a below-grade concrete basement floor I want to serve as > my workshop and would love it if your approach mightwork. But the moisture [quoted text clipped - 4 lines] > basement floor and medical advice is "don't spend time standing on > concrete!" ...
Hardwood flooring is definitely not an option for below grade. Unless the slab was laid w/ an effective moisture barrier underneath and otherwise prepared, it may be difficult to do much in a solid flooring.
Possible alternative would be the perforated cushioned pads for a walking surface. I use livestock padding as it's significantly cheaper than most sold as comfort pads.
resrfglc - 20 Dec 2006 18:30 GMT "I use livestock padding "
I was pricing that at Tractor Supply and bought some of those 24" square foam interlocking sections at Big Lots (6 for $12) to serve immediately.
But the concern I have is that they may hold the moisture beneath and create a layer of mold between concrete and "livestock pads" which appear non-porous.
Do you ever check beneath them to see if anything's growing there?
>> "using 3m blue tape" >> [quoted text clipped - 26 lines] > walking surface. I use livestock padding as it's significantly cheaper > than most sold as comfort pads. Bill in Detroit - 23 Dec 2006 07:33 GMT > "I use livestock padding " > [quoted text clipped - 6 lines] > > Do you ever check beneath them to see if anything's growing there? I use a 24"x24"x 3/4" foam padding product I got from an auto supply store. It does trap moisture underneath (house built in 1945) so I stand the pads, one each in front of lathe and TS, up on edge when I am vacuuming and leave them up until time to use them again.
Works for me. YMMV
Bill
--- avast! Antivirus: Outbound message clean. Virus Database (VPS): 0662-0, 12/22/2006 Tested on: 12/23/2006 2:33:46 AM avast! - copyright (c) 1988-2006 ALWIL Software. http://www.avast.com
resrfglc - 23 Dec 2006 10:13 GMT "Works for me"
Yep, uunderstand. Thanks for teh FB.
>> "I use livestock padding " >> [quoted text clipped - 22 lines] > avast! - copyright (c) 1988-2006 ALWIL Software. > http://www.avast.com Kay Lancaster - 23 Dec 2006 22:42 GMT > I use a 24"x24"x 3/4" foam padding product I got from an auto supply > store. It does trap moisture underneath (house built in 1945) so I stand > the pads, one each in front of lathe and TS, up on edge when I am > vacuuming and leave them up until time to use them again. In a lab with concrete floors (and no moisture barrier beneath), I used the heavy black "welcome mats" with rubber fingers in front of each major work area. I turned the mats upside down so there was some air circulation under the mat, and I had a solid surface to stand on. Worked quite well.
Kay
dpb - 27 Dec 2006 00:29 GMT > "I use livestock padding " > [quoted text clipped - 6 lines] > > Do you ever check beneath them to see if anything's growing there? ...
Specifically, I mentioned...
> > Possible alternative would be the perforated cushioned pads for a > > walking surface. I use livestock padding as it's significantly cheaper > > than most sold as comfort pads. But, I don't have them in a basement, so if it's particularly damp I suppose it _could_ be a problem. But, in the shop I only place them in the places where I normally stand frequently, like in front of the tablesaw, bench, etc., etc. Consequently, they're easy enough to flip over and move if want one somewhere else temporarily. The particular ones I was thinking of aren't solid, either, so that the amount of moisture entrapped wouldn't be that much (again, unless it were _really_ damp). They have about a 50% or more open spacing. Does mean they collect the sawdust in the holes, but as they're not that heavy, as noted above, all it takes is flipping one over to sweep. Most of the time the shop vac w/ the floor sweep tool is enough, anyway, though.
HTH...
OBTW, they were even cheaper than the solid ones by almost the 50% factor so I gather they're basically priced on the amount of material since they're mostly an artificial rubber, they're pretty much tied to petro prices. I also have a thin, salvaged truck bed liner that I didn't want in the truck that came w/ the used truck I bought that I've tossed on the floor in front of the chopsaw bench -- it isn't nearly as comfortable as the others, but even it helps noticeably both for softer standing and not so cold in winter.
Swingman - 20 Dec 2006 12:17 GMT <lefebvre@iwavesolutions.com> wrote in message
> Is this a crazy idea? For most builders (at least in this area), perhaps. Mainly because it is a departure from a method that _has_ stood the test of time, and one with well known and relatively easy/cost effective solutions to problems that may arise in the future for both the builder and homeowner.
For you, that does not mean that it won't work, but that only time will tell.
 Signature www.e-woodshop.net Last update: 12/19/06
Epictitus - 20 Dec 2006 13:12 GMT Why not consider a floating floor product i.e. engineered wood floor? The finishes available are durable (probably more durable than finish in place floors) and the seams can be tight and near invisible. And it goes in very fast. Use a good quality underlay.
> Thanks for the tips. It seems that many installation provisions > recomended boil down to a nail down type installation, either over a [quoted text clipped - 43 lines] >> better in this climate than hardwood floors laid on the subfloor of a >> crawlspace foundation. dpb - 20 Dec 2006 14:40 GMT > Thanks for the tips. It seems that many installation provisions > recomended boil down to a nail down type installation, either over a [quoted text clipped - 16 lines] > > Is this a crazy idea? ...
That's _ONE_ year for a flooring material that can last 200 or more -- not a very long time yet.
What I see as potential issues --
1. The tongue and groove of strip flooring aren't made to fit to a close tolerance for a glue joint. You don't mention what you used as the glue, but I would be quite surprised if you can find a way that these joints will last for a long period of time w/o eventually failing at the joint. Remember, this is potentially a multiple-lifetime flooring material and you've seen the results of your experiment for only _one_ year so far.
2. For a large floor, you don't have any way to prevent movement between boards over time other than the above glue joint -- rarely (as in never) have I seen strip flooring which didn't need at least some persuasion when initially being laid to close the joints and for a large area I think you'll run into problems of a very high rejection/wastage rate if you require every piece to be absolutely true its entire length in order to pull joints tight during the installation. The supplier will not think these pieces out of spec as they would work fine w/ recommended installation techniques so this will raise cost.
3. You don't say, but I'm assuming you didn't finish four sides (top, bottom, two ends -- sides obviously can't be if gluing). Thus, as w/ a convential strip floor, you still have three of the four sides available for moisture movement. Over one year, maybe you got by, over a long-haul I don't expect you to be so lucky. Finishing the bottom/ends might help a little, but finishes don't stop moisture, transfer, they slow it down.
Overall, I think you're risking a pretty sizable investment on an unproven method of installation when proven methods are available. If it were something that would be relatively easy to fix later, I'd say "sure, give it a shot", but once this is down in an entire house, _if_ it does fail, you've got a real mess on your hands plus quite an expense. I'm w/ the other poster who suggested if you want a floating floor, buy a product designed to be installed that way.
It's your house and your money, but I'm not that kind of a risk-taker.
IMO, YMMV, $0.02, etc., etc., etc., ... :)
John Grossbohlin - 20 Dec 2006 19:13 GMT > Thanks for the tips. It seems that many installation provisions > recomended boil down to a nail down type installation, either over a [quoted text clipped - 16 lines] > > Is this a crazy idea? If high and/or stable humidity is a year round thing in Hawaii floating shouldn't be needed as things would tend to stay constant (wet) and thus stay put. Letting the flooring acclimate in the house and then installing it would suffice. It's the seasonal variations and/or not letting the flooring acclimate that tend to cause problems.
What about termites though?
DRIcore subflooring would be an option. Termites may not like this stuff at all due to all of the adhesives and plastics. It might be worth checking that out. http://www.dricore.com/en/eindex.htm
Another option, again with the termites in mind, would be PT sleepers to flatten and PT ply subfloor, vapor/squeak barrier and then nail down your wood finish floor. If the concrete is relatively flat PT plywood glued down may work just fine however you may need two layers to deal with the nail/staple penetration.
I'd be concerned with the termites if untreated wood were basically in contact with concrete. They'd likely find it sooner or later.
John
Oren - 21 Dec 2006 01:05 GMT > However, what about my orignal idea of actually "floating" it? Follow the manufacturer's instruction. If not, a warranty is immediately voided. You pay premium in HI for products now.
Adhesives, as I understand now have moisture barrier quialities.
Prepare the floor, get a good adhesive and put the floor down. Floating in your test room may not have the same end result in the new room.
>Here is what I did on my test room: -- Oren
"Well, it doesn't happen all the time, but when it happens, it happens constantly."
marc rosen - 19 Dec 2006 22:03 GMT Hello Marc, It's Marc from recdotwindsurfing (and the old King of The Cape days. I miss going to the Brazilian Grill in Hyannis). How are you and Iyesha? I've seen some of your windsurf posts on recdot recently. Sorry I don't have any advice for your floor question. But now if you want to know how much downhaul to put on your sail, well maybe. Take care and Merry Christmas/Happy New Year.
T.O.M. (The Other Marc)
> I am interested in floating a solid hardwood plank floor (3/4" x 3"). > Has anyone successfully done this? I am leary of glue down application [quoted text clipped - 12 lines] > > -Marc efgh - 20 Dec 2006 16:50 GMT >I am interested in floating a solid hardwood plank floor (3/4" x 3"). > Has anyone successfully done this? I am leary of glue down application [quoted text clipped - 12 lines] > > -Marc Holmes on Homes had an episode where the homeowner had hardwod flooring instaled over concrete. While I can't remember the specifics of the issues, the reader's digest version is that it, the flooring and the plywood subfloor, rotted out in a relatively short period of time. Mike went through the trouble of making sure there were no other water leaks that could have caused the problem. He even drilled into the concrete slab that was poured 25 years ago only to discover that it was the proper thickness, the styrofoam under the slab was fine and the dirt below that was dry. I think he concluded that the moisture in the concrete was causing the flooring/subfloor to rot. He ended up putting down a slate tile with an electric heating pad underneath.
resrfglc - 20 Dec 2006 18:30 GMT "He ended up putting down a slate tile "
For a shop floor, tile isn't much better than concrete - or am I missing something?
>>I am interested in floating a solid hardwood plank floor (3/4" x 3"). >> Has anyone successfully done this? I am leary of glue down application [quoted text clipped - 24 lines] > causing the flooring/subfloor to rot. He ended up putting down a slate > tile with an electric heating pad underneath. efgh - 20 Dec 2006 18:55 GMT > "He ended up putting down a slate tile " > > For a shop floor, tile isn't much better than concrete - or am I missing > something? Yes. The OP installed the hardwood flooring in his house. Mike Holmes put it in a kitchen. After re-reading my post, I omitted where in the house the issue was. My apologies.
>>>I am interested in floating a solid hardwood plank floor (3/4" x 3"). >>> Has anyone successfully done this? I am leary of glue down application [quoted text clipped - 24 lines] >> causing the flooring/subfloor to rot. He ended up putting down a slate >> tile with an electric heating pad underneath.
|
|
|