Methos - 25 Aug 2006 02:58 GMT
the way a GFCI functions, would it trip
if a bad connection were made to it ?

(if say, a terminal with the hot or
neutral wasn't screwed down tight &
a plugged in load drew current causing
the terminal to warm up - would the
GFCI trip ?)
Jonny - 25 Aug 2006 03:28 GMT
http://ts.nist.gov/ts/htdocs/210/gsig/apec-elec/gannon.ppt

The load's current use is sensed by the GFCI whether wired dubiously as in
the example you imposed.

The problem child is when the grounding and neutral are swapped.

Arcing, as implied by your example, needs an AFI circuit for detection.
Signature

Jonny

>
> the way a GFCI functions, would it trip
[quoted text clipped - 5 lines]
> the terminal to warm up - would the
> GFCI trip ?)
Methos - 25 Aug 2006 13:38 GMT
> http://ts.nist.gov/ts/htdocs/210/gsig/apec-elec/gannon.ppt
>
[quoted text clipped - 13 lines]
> > the terminal to warm up - would the
> > GFCI trip ?)

thanks everyone for the responses.

the powerpoint link was very informative.

if i understood it correctly, any current differential
> 5ma between hot & neutral would cause a trip.

if one terminal has contact resistance (loose),
wouldn't the current flow on that leg be reduced
by the amount of resistance ? and therefore trip
the GFCI ? (since it would see less on one leg,
vs the other - or am I misinterpreting, since a
hot/load/neutral circuit is basically in series,
and current is only depended on how much the
device draws?)
John G - 25 Aug 2006 13:46 GMT
>> http://ts.nist.gov/ts/htdocs/210/gsig/apec-elec/gannon.ppt
>>
[quoted text clipped - 31 lines]
> and current is only depended on how much the
> device draws?)

Both wires are part of the same series circuit and the current will be
the same whileever there is no other path (ground).

Current in = current out.

The resistance of the contact will be part of the impedance (along with
the real load) that determines the magnitude of the current.
Signature

John G

Wot's Your Real Problem?

mm - 25 Aug 2006 04:14 GMT
>the way a GFCI functions, would it trip
>if a bad connection were made to it ?
[quoted text clipped - 4 lines]
> the terminal to warm up - would the
> GFCI trip ?)

I don't think so.  Why would the resistance of a bad connection be any
different from the resistance of a light bulb.

I wouldn't assume there will be arcing just because a connection isn't
tight enough.  So I wouldn't assume that even an arc fault circuit
breaker would be tripped by a loose connection.  Am I right or wrong?
LightsAREon - 25 Aug 2006 04:25 GMT
>> the way a GFCI functions, would it trip
>> if a bad connection were made to it ?
[quoted text clipped - 11 lines]
> tight enough.  So I wouldn't assume that even an arc fault circuit
> breaker would be tripped by a loose connection.  Am I right or wrong?

Methos

A GFIC is made to trip on sudden line voltage changes.  A slow warm up
would not trip the built in breaker.  This very problem cause a house
fire that burned a third of my parents house to the ground.  Two wires
in some old Romex touched and caused a slow short but it was not enough
to trip the breakers.  Therefore, it warmed up long enough to catch fire.

GFIC's are a nice safety feature but it certainly doesn't catch all problems
Bud-- - 26 Aug 2006 07:55 GMT
>>> the way a GFCI functions, would it trip
>>> if a bad connection were made to it ?
[quoted text clipped - 4 lines]
>>> the terminal to warm up - would the
>>> GFCI trip ?)

I agree with others that a GFCi wouldn't trip on a loose connection.

>> I don't think so.  Why would the resistance of a bad connection be any
>> different from the resistance of a light bulb.
>>
>> I wouldn't assume there will be arcing just because a connection isn't
>> tight enough.  So I wouldn't assume that even an arc fault circuit
>> breaker would be tripped by a loose connection.  Am I right or wrong?

A loose connection can produce enough heat to start a fire without
arcing (a "glowing" connection). Late stages in failure are likely to arc.

AFCIs sense "parallel" arcs - from hot-to-neutral (a "fault", the F in
AFCI). Starting in 2008 the NEC requires them to also detect "series"
arcs, as in a loose connection. As far as I know, no current AFCIs
detect series arcs, so none would detect a loose connection.

> Methos
>
[quoted text clipped - 6 lines]
> GFIC's are a nice safety feature but it certainly doesn't catch all
> problems

GFCIs trip on a difference in current between the hot and neutral, not
line voltage changes. They are primarily for electrocution protection.

The "slow short" you describe, an arc that trips a breaker slowly, if at
all, is exacty what AFCIs are designed to protect against. A more likely
cause is probably an abused extension cord.

AFCIs also include 30mA ground fault protection (GFCIs have 5mA
protection). The idea is, I think, that if a ground wire is adjacent, a
hot-to-neutral arc is likely to also become hot-to-ground.

bud--
LightsAREon - 26 Aug 2006 17:20 GMT
>>>> the way a GFCI functions, would it trip
>>>> if a bad connection were made to it ?
[quoted text clipped - 46 lines]
>
> bud--

Methos
It sounds like bud has the right answer.  I hadn't heard about the
upcoming AFIC's but will certainly pass the info on to everyone at my
office (I'm a construction administrator for a large architectural
firm).  Thanks bud for the education.
LightsAREon
PPS - 28 Aug 2006 22:20 GMT
I don't believe it's "upcoming". I think that all AFCI's currently have 30ma
ground fault protection for equipment.

> Methos
> I hadn't heard about the upcoming AFIC's but will certainly pass the info
> on to everyone at my office (I'm a construction administrator for a large
> architectural firm).  Thanks bud for the education.
> LightsAREon
Ook - 29 Aug 2006 00:53 GMT
What is "30ma ground fault protection"? It takes less then 30 mA to kill a
man.

>I don't believe it's "upcoming". I think that all AFCI's currently have
>30ma ground fault protection for equipment.
[quoted text clipped - 4 lines]
>> architectural firm).  Thanks bud for the education.
>> LightsAREon
gfretwell@aol.com - 29 Aug 2006 04:05 GMT
On Mon, 28 Aug 2006 16:53:37 -0700, "Ook" <Ook Don't send me any
freakin' spam at zootal dot com delete the Don't send me any freakin'
spam> wrote:

>What is "30ma ground fault protection"? It takes less then 30 mA to kill a
>man.
They call it Ground-Fault Protection of Equipment when it is at the
30ma level.
BTW get used to AFCIs. They will be on all 120v  15 and 20a circuits
in a dwelling in 2008 if the code goes as drafted. Comments are still
open until October.
Bud-- - 29 Aug 2006 14:45 GMT
> On Mon, 28 Aug 2006 16:53:37 -0700, "Ook" <Ook Don't send me any
> freakin' spam at zootal dot com delete the Don't send me any freakin'
[quoted text clipped - 5 lines]
> They call it Ground-Fault Protection of Equipment when it is at the
> 30ma level.

Yea - it is to detect the arc, not protect people. AFCIs can have a 5 mA
ground fault trip and be used as both AFCI and GFCI. It would require 2
test buttons. Probably would see them if the code change below goes into
effect.

To PPS - I presume "upcoming" is the requirement to detect "series" arcs
starting 2008, not 30mA ground fault trip.

> BTW get used to AFCIs. They will be on all 120v  15 and 20a circuits
> in a dwelling in 2008 if the code goes as drafted. Comments are still
> open until October.

Considering the new AFCIs aren't on the market (or are they recently
out?), and it is only about 1.5 years for field experience until they
are required in 2008, it seems like requiring the new AFCIs in all
15/20A dwelling circuits is not a great idea (whatever the wisdom of
requiring the current AFCIs is). Bet there are plenty of comments on
that code change.

An interesting piece on AFCIs, including why normal breakers are
inadequate for arcs and arcs that shouldn't trip them is at:
http://www.cpsc.gov/volstd/afci/AFCIFireTechnology.pdf

bud--
Mark Lloyd - 29 Aug 2006 19:20 GMT
>On Mon, 28 Aug 2006 16:53:37 -0700, "Ook" <Ook Don't send me any
>freakin' spam at zootal dot com delete the Don't send me any freakin'
[quoted text clipped - 7 lines]
>in a dwelling in 2008 if the code goes as drafted. Comments are still
>open until October.

Wouldn't that be all circuits in new construction?
Signature

Mark Lloyd
http://notstupid.laughingsquid.com

"Democracy is two wolves and a lamb voting on what
to have for lunch. Liberty is a well armed lamb
contesting the vote." - Benjamin Franklin

gfretwell@aol.com - 30 Aug 2006 01:28 GMT
>Wouldn't that be all circuits in new construction?

Usually it would be all the 120v ones.
Mark Lloyd - 30 Aug 2006 04:43 GMT
>>Wouldn't that be all circuits in new construction?
>
>Usually it would be all the 120v ones.

There's no 240v AFCIs?
Signature

Mark Lloyd
http://notstupid.laughingsquid.com

"Democracy is two wolves and a lamb voting on what
to have for lunch. Liberty is a well armed lamb
contesting the vote." - Benjamin Franklin

gfretwell@aol.com - 30 Aug 2006 06:08 GMT
>>>Wouldn't that be all circuits in new construction?
>>
>>Usually it would be all the 120v ones.
>
>There's no 240v AFCIs?
I believe there may be 240v AFCIs but they are not mandated in the
code yet.
PPS - 31 Aug 2006 00:21 GMT
Only requirement I'm aware of where GFPE's (30 ma GFCI) are required in the
2005 NEC is Section 426.28.

> What is "30ma ground fault protection"? It takes less then 30 mA to kill a
> man.
David Combs - 24 Sep 2006 01:33 GMT
>A loose connection can produce enough heat to start a fire without
>arcing (a "glowing" connection). Late stages in failure are likely to arc.
[quoted text clipped - 27 lines]
>
>bud--

What is an AFIC?

Thanks!

David
Sam E - 24 Sep 2006 04:54 GMT
[snip]

>What is an AFIC?

An Arc Fault Interrupted Circuit. A circuit that has no current in it
because you didn't use an AFCI, your house was on fire, and the fire
department cut off the power.

>Thanks!
>
>David
Bud-- - 26 Sep 2006 07:49 GMT
>>A loose connection can produce enough heat to start a fire without
>>arcing (a "glowing" connection). Late stages in failure are likely to arc.
[quoted text clipped - 33 lines]
>
> David

Arc Fault Circuit Interrupter. The AFCI breakers look like, and wire
like GFCIs. AFCIs trip on arcs. The NEC requires them on new circuits to
bedrooms. The proposed 2008 NEC requires them for all residential 15 and
20A circuits IIRC (could still be changed though).

A good paper from the Consumer Product Safety Commission on AFCIs is at
http://www.cpsc.gov/volstd/afci/AFCIFireTechnology.pdf
It explains the rationalle for using AFCIs describes how they work.

bud--
phil-news-nospam@ipal.net - 26 Sep 2006 11:01 GMT
In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:

| Arc Fault Circuit Interrupter. The AFCI breakers look like, and wire
| like GFCIs. AFCIs trip on arcs. The NEC requires them on new circuits to
| bedrooms. The proposed 2008 NEC requires them for all residential 15 and
| 20A circuits IIRC (could still be changed though).

And AFCI-only device could be made to work without accessing the neutral
of the circuit involved.  The issue is the AFCI device needs to use power
to function.  Possibly that is the only purpose of the neutral pigtail if
the device does not include any GFCI function.

I hope the change goes through.  But I would like to see local AHJ rules
that permit case-by-case exceptions to be made where AFCI devices are
found to be incompatible with certain appliances.

And regarding the issue of putting smoke detectors on AFCI protected
circuits.  The simple solution is keep receptacle circuits and lighting
circuits separate, and put the smoke detectors on the lighting circuits.
Those circuits should have much less instance of nuisance trips, and
would more readily be noticed if they are opened, in case the smoke
detector false to alarm.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-09-26-0455@ipal.net |
|------------------------------------/-------------------------------------|
mrsgator88 - 26 Sep 2006 13:49 GMT
> And regarding the issue of putting smoke detectors on AFCI protected
> circuits.  The simple solution is keep receptacle circuits and lighting
> circuits separate, and put the smoke detectors on the lighting circuits.
> Those circuits should have much less instance of nuisance trips, and
> would more readily be noticed if they are opened, in case the smoke
> detector false to alarm.

We had to have smoke detectors on a separate dedicated circuit.  Our
contractor decided not to sub out the electrical work, and sure looked upset
when he learned he had to rewire four levels of smoke detectors.

S
Bud-- - 27 Sep 2006 06:28 GMT
> In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:
>
[quoted text clipped - 7 lines]
> to function.  Possibly that is the only purpose of the neutral pigtail if
> the device does not include any GFCI function.

But all AFCIs include a 30mA GFCI as part of the protection. (That is
not the same as a 6mA GFCI for shock protection of people.)

> And regarding the issue of putting smoke detectors on AFCI protected
> circuits.  The simple solution is keep receptacle circuits and lighting
> circuits separate, and put the smoke detectors on the lighting circuits.
> Those circuits should have much less instance of nuisance trips, and
> would more readily be noticed if they are opened, in case the smoke
> detector false to alarm.

Just to be clear, lighting  circuits that include bedrooms have to be on
an AFCI. (I think that is what you said.)

bud--
phil-news-nospam@ipal.net - 27 Sep 2006 21:56 GMT
In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:
|> In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:
|>
[quoted text clipped - 10 lines]
| But all AFCIs include a 30mA GFCI as part of the protection. (That is
| not the same as a 6mA GFCI for shock protection of people.)

I've seen some that don't.  Those were from Cutler-Hammer, the company
that makes AFCI without GFCI, AFCI with 30maGFCI, and AFCI with 6maGFCI.

If the NEC ends up requiring the GFCI function, then the ones without
GFCI would likely end up being no longer made.  But right not it is not
clear what the NEC requires NOW (2005 code) or will require (2008 code).
All we know is that the scope of where AFCI is required appears to be
expanding.

|> And regarding the issue of putting smoke detectors on AFCI protected
|> circuits.  The simple solution is keep receptacle circuits and lighting
[quoted text clipped - 5 lines]
| Just to be clear, lighting  circuits that include bedrooms have to be on
| an AFCI. (I think that is what you said.)

All the circuits supplying outlets in the bedrooms must be AFCI protected.

The issue with smoke detectors is more complex.  I do believe they must
be on AFCI, and I think that is appropriate.  I do not expect the smoke
detectors to be any source of nuisance trips.  Thus it might seem to be
a good plan to put them all on their own circuit.  But I don't trust that
they will alarm when the power is lost.  The reason is because that would
cause problems in utility outages.  Do you want all your smoke detectors
beeping when a storm knocks out your power?  But what if the branch circuit
the smoke detectors are on loses power.  You might not even notice that a
problem exists.  Connecting smoke detectors with receptacles is a bad idea
becauseof two reasons.  Either the receptacle might not even get used, or
the receptacle's usage might be the source of excess nuisance trips.  That
could compromise the safety of the smoke detectors.  My idea is to put
them on the same circuit as regularly used overhead lights, such as hall
lights or stairway lights.  That way, if there is a circuit trip that does
affect the smoke detectors, you will be alerted to a problem with that
breaker, and motivated to correct it.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-09-27-1544@ipal.net |
|------------------------------------/-------------------------------------|
Thomas D. Horne, FF EMT - 28 Sep 2006 03:20 GMT
> In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:
> |> In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:
[quoted text clipped - 49 lines]
> affect the smoke detectors, you will be alerted to a problem with that
> breaker, and motivated to correct it.

Smoke detectors that are designed to be interconnected will usually have
a backup battery and will chirp every so often if power is lost.
Signature

Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.

Bud-- - 28 Sep 2006 08:47 GMT
>> In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:
>> |> In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:
[quoted text clipped - 15 lines]
>> I've seen some that don't.  Those were from Cutler-Hammer, the company
>> that makes AFCI without GFCI, AFCI with 30maGFCI, and AFCI with 6maGFCI.

Have a reference handy for AFCIs without 30mA ground fault detection?

>> If the NEC ends up requiring the GFCI function, then the ones without
>> GFCI would likely end up being no longer made.  But right not it is not
[quoted text clipped - 36 lines]
>> affect the smoke detectors, you will be alerted to a problem with that
>> breaker, and motivated to correct it.

(There was a proposal for the 2008 NEC to require that but it was rejected.)

> Smoke detectors that are designed to be interconnected will usually have
> a backup battery and will chirp every so often if power is lost.

Do they chirp if the battery is dead? Removed? I havn't played with them.

The way I understand the 2008 NEC-ROP, NFPA 760 requires smoke detectors
that are on AFCI circuits have a secondary power source (battery).
Another hidden requirement.

IMHO requiring smoke detectors to be on an AFCI circuit lowers overall
fire safety and is dumb.

bud--
phil-news-nospam@ipal.net - 28 Sep 2006 12:55 GMT
In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:

| Have a reference handy for AFCIs without 30mA ground fault detection?

Some have 5ma GFCI and some have no GFCI:

Page 22:
http://www.eatonelectrical.com/unsecure/cms1/TB00300001E.PDF

Pages 3 and 4:
http://www.eatonelectrical.com/unsecure/cms1/TD00308001E.PDF

Page 1:
http://www.eatonelectrical.com/unsecure/cms1/TD01201036E.PDF

| The way I understand the 2008 NEC-ROP, NFPA 760 requires smoke detectors
| that are on AFCI circuits have a secondary power source (battery).
| Another hidden requirement.
|
| IMHO requiring smoke detectors to be on an AFCI circuit lowers overall
| fire safety and is dumb.

I'm not convinced of that, yet.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-09-28-0650@ipal.net |
|------------------------------------/-------------------------------------|
PPS - 28 Sep 2006 23:35 GMT
Those without GFCI protection are intended for use in habitable and
non-habitable spaces not requiring ground fault protection (living rooms and
the like.)

Those with 5ma GFCI protection are intended to serve bathrooms, kitchens and
anywhere where a standard GFCI is required.

Those with 30ma GFCI is designed to serve residential equipment noted in the
NEC requiring 30 ma GFCI (actually termed GFEP to differentiate between the
two.) Article 426.28 only requires ground fault protection for equipment, no
personnel and that's to only place it can be used to meet code. To protect
personnel, you must use 5ma protection.

> In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:
>
> | Have a reference handy for AFCIs without 30mA ground fault detection?
>
> Some have 5ma GFCI and some have no GFCI:
phil-news-nospam@ipal.net - 29 Sep 2006 01:28 GMT
In alt.engineering.electrical PPS <webmaster@npcc.net> wrote:

| Those without GFCI protection are intended for use in habitable and
| non-habitable spaces not requiring ground fault protection (living rooms and
[quoted text clipped - 8 lines]
| personnel and that's to only place it can be used to meet code. To protect
| personnel, you must use 5ma protection.

This is along the lines of what I expected, and certainly sounds very
reasonable.  Still, the required ground fault protection can be had with
an AFCI that has no GFCI, or only has 30ma GFCI, as long as the 5ma GFCI
receptacles are also used, where the GFCI people protection is required.
Whether one would want to do it that way is another matter.

In a bathroom, there is an advantage to having the ability to reset the
GFCI device right there.  That advantage may or may not be relevant for
a kitchen.  Other areas like a garage are probably not much of a concern.

I have been told, but have never sacrificed a device to verify, or set up
the appropriate test, that GFCI receptacles open BOTH the hot wire AND the
neutral wire when they trip.  If so, why is that?  Is it to offer at least
some protection even when the device is miswired?  Or is there even some
risk with voltages on the neutral wire?

I do believe some neutral wire risk exists.  It's certainly not as much as
for the hot wire, usually in terms of voltage, and in terms of exposure
events.  One example of when the risk is high is when there is a open in
in the supply neutral.  But the chance of that happening coincident with
contacting the neutral to ground, is much lower than either alone.  The
other risk is the voltage present as a function of the voltage drop along
the supply neutral from the point of bonding to the point of contact.
That's generally a very low voltage, though it can vary with loading on
the system.  Still, I'd feel safer having an interruption mechanism that
will open BOTH wires together when tripped.

Suppose you have an AFCI that includes GFCI protection, either at the 5ma
level or the 30ma level, followed by a GFCI receptacle.  Leakage from the
neutral to ground would still result in a trip.  But can it be guaranteed
that the receptacle device will always open?  Perhaps the breaker will open
first, and de-energize the circuit before the receptacle can open, leaving
the neutral wire still connected.  To be assured that the receptacle will
trip, I'd have to have no GFCI in the breaker, and place the GFCI protection
in the receptacle, assuming it is designed to open the neutral.

If I am forced to put GFCI protection in the breaker along with the AFCI
protection, or if GFCI receptacles don't actually have neutral contacts
that can be opened, I do have a fallback plan.  I would run the circuit
through a secondary box containing a 2-pole normally open electrically
closed contactor.  The circuit would run through these contacts.  The
coil would be powered from the supply side.  If the breaker opens the
hot wire, the coil will de-energize and open both wires.  It won't be as
quick an open since such contactors aren't listed for GFCI protection.
But at least it will be something that can prevent certain problems.
For shared neutral circuits, this would be a 3-pole contactor with a 240
volt coil.  These are avalable from Square-D and Cutler-Hammer.  One issue
that some people might be concerned with is the constant power used by the
coil, 24x365xN.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-09-28-1854@ipal.net |
|------------------------------------/-------------------------------------|
Bud-- - 29 Sep 2006 16:47 GMT
> In alt.engineering.electrical PPS <webmaster@npcc.net> wrote:
>
[quoted text clipped - 10 lines]
> | personnel and that's to only place it can be used to meet code. To protect
> | personnel, you must use 5ma protection.

30mA ground fault detection in an AFCI is for arc protection. Far as I
know all AFCIs include it (though I need to look harder at phil's 2nd
link). Arcs can produce carbon paths which, if a ground is available,
can produce ground fault currents. That may produce a trip before there
is an arc or before an arc is detected.

In the Consumer Product Safety Commission paper at:
http://www.cpsc.gov/volstd/afci/AFCIFireTechnology.pdf
that is explained on pdf page 14.

Phil has a link in another thread to:
http://www.eatonelectrical.com/unsecure/cms1/AFCI_UL_SPECIAL_SERVICES_INVESTIGAT
ION.PDF

which is a UL investigation showing that a "glowing connection" at a
receptacle binding screw may (or may  not) cause an AFCI trip through
the 30mA ground fault function.

> This is along the lines of what I expected, and certainly sounds very
> reasonable.  Still, the required ground fault protection can be had with
[quoted text clipped - 11 lines]
> some protection even when the device is miswired?  Or is there even some
> risk with voltages on the neutral wire?

I have read in newsgroups (so it must be true) that both poles are
opened for hot-neutral-reverse protection.

GFCIs (5mA) are now required to not work with reverse load-line terminal
wiring. (Previously the load terminals connected to the receptacle.) I
don't think you can do that without double pole contacts line-receptacle
and line-load. And I don't think it can be done without that being a NO
contact that requires the device to be powered to connect (which it
wouldn't be if the line-side neutral was open).

In both cases testing can be easily done without a hammer but so far I
have been too lazy.

> I do believe some neutral wire risk exists.  It's certainly not as much as
> for the hot wire, usually in terms of voltage, and in terms of exposure
[quoted text clipped - 15 lines]
> trip, I'd have to have no GFCI in the breaker, and place the GFCI protection
> in the receptacle, assuming it is designed to open the neutral.

bud--
PPS - 29 Sep 2006 23:03 GMT
> 30mA ground fault detection in an AFCI is for arc protection. Far as I
> know all AFCIs include it (though I need to look harder at phil's 2nd
> link).

Here's a good place to learn more.
http://www.cpsc.gov/CPSCPUB/PUBS/afcifac8.pdf#search=%22afci%20ground%20fault%22
phil-news-nospam@ipal.net - 30 Sep 2006 13:48 GMT
In alt.engineering.electrical PPS <webmaster@npcc.net> wrote:

|> 30mA ground fault detection in an AFCI is for arc protection. Far as I
|> know all AFCIs include it (though I need to look harder at phil's 2nd
|> link).
|
| Here's a good place to learn more.
| http://www.cpsc.gov/CPSCPUB/PUBS/afcifac8.pdf#search=%22afci%20ground%20fault%22

Sounds like we are now back to the beginning.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-09-30-0748@ipal.net |
|------------------------------------/-------------------------------------|
PPS - 03 Oct 2006 00:40 GMT
A "neutral" is not defined in the NEC, but is described in Article
310.15(B)(4) as carrying "only the unbalanced current from other
conductors...".

In a 120 volt (lighting) circuit, the current is carried on both the white
(or "grounded") conductor and an "ungrounded (usually black, but not
necessarily) conductor.
The term "neutral" refers to the neutral connection at the transformer; the
center-tap. In a pure 240 volt circuit, current flows on the two phase
conductors and a white (or grounded) conductor in not even needed. By
introducing 120 volt circuits, the white forms one of the return legs, and
carries current. (240 v between the ungrounded legs, 120 v from either leg
to the neutral.)

In Europe, the term "neutral" does include a grounded conductor in a 120 v
circuit. In the states the term is used interchangeably but in error.

> In alt.engineering.electrical PPS <webmaster@npcc.net> wrote:
> |
[quoted text clipped - 14 lines]
> |
> |------------------------------------/-------------------------------------|
phil-news-nospam@ipal.net - 04 Oct 2006 14:09 GMT
In alt.engineering.electrical PPS <webmaster@npcc.net> wrote:

| A "neutral" is not defined in the NEC, but is described in Article
| 310.15(B)(4) as carrying "only the unbalanced current from other
| conductors...".

"Neutral conductor" is defined in the NEC.  The term is used in many places.
I fully understand what a neutral is.  Are you raising an issue about its
common or formal usage?

| In a 120 volt (lighting) circuit, the current is carried on both the white
| (or "grounded") conductor and an "ungrounded (usually black, but not
| necessarily) conductor.

If you are wanting to get very specific, it's the insulators that have the
color.  The current is carried on the (usually) copper metal (with a magnetic
field, of course).

The code requires the grounded conductor be identified well (e.g. continuous
color, not just marked at each end).  Others have more leeway.

| The term "neutral" refers to the neutral connection at the transformer; the
| center-tap. In a pure 240 volt circuit, current flows on the two phase
| conductors and a white (or grounded) conductor in not even needed. By
| introducing 120 volt circuits, the white forms one of the return legs, and
| carries current. (240 v between the ungrounded legs, 120 v from either leg
| to the neutral.)

You could tap the transformer off-center a bit if you wanted to and have
115 volts on one side and 125 volts on the other side.  Would you call that
a "neutral"?

So tell me ... what happens if you have a couple of very low power factor
loads, one on each 120 volt side, where one is very inductive and the other
is very capacitive?  Now how much current flows on the "neutral"?

| In Europe, the term "neutral" does include a grounded conductor in a 120 v
| circuit. In the states the term is used interchangeably but in error.

I see very little use in error in the US.  Neutral does not mean grounded,
but it generally implies that because that is the required way to wire it
up.  See NEC 250.26(2).  The two terms "neutral conductor" and "grounded
conductor" do have different meanings, but are associated with the same
wire because that is the required way.

Single phase in Europe is generally 2-wire service.  You can still call one
wire neutral because it may well be the wire connected to the real neutral
point in either a single phase transformer (center tapped 230/460) or a
three phase transformer (connected to the star common).  But it is grounded
and thus (also) correct to call it a grounded conductor.  If the service is
coming from a 2-wire transformer all by itself, then it's not really neutral;
it's just grounded.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-10-04-0750@ipal.net |
|------------------------------------/-------------------------------------|
Andrew Gabriel - 05 Oct 2006 09:25 GMT
> In Europe, the term "neutral" does include a grounded conductor in a 120 v
> circuit. In the states the term is used interchangeably but in error.

In Europe, there are no 120V circuits, and "neutral" is a supply
current carrying conductor which is at or near ground potential.

Signature

Andrew Gabriel

phil-news-nospam@ipal.net - 05 Oct 2006 11:51 GMT
In alt.engineering.electrical Andrew Gabriel <andrew@cucumber.demon.co.uk> wrote:
|> In Europe, the term "neutral" does include a grounded conductor in a 120 v
|> circuit. In the states the term is used interchangeably but in error.
|
| In Europe, there are no 120V circuits, and "neutral" is a supply
| current carrying conductor which is at or near ground potential.

But that doesn't really change the meaning's origin.  The first power
systems were three phase to drive motors.  I don't know if delta was
used much way back when, but with star/wye configurations, you do have
a genuine neutral.  When single phase at 240v is taken from that, the
neutral is still there.  It just doesn't have enough phases brought
in to take the neutralizing role there.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-10-05-0547@ipal.net |
|------------------------------------/-------------------------------------|
Andrew Gabriel - 05 Oct 2006 14:10 GMT
> In alt.engineering.electrical Andrew Gabriel <andrew@cucumber.demon.co.uk> wrote:
>|> In Europe, the term "neutral" does include a grounded conductor in a 120 v
[quoted text clipped - 9 lines]
> neutral is still there.  It just doesn't have enough phases brought
> in to take the neutralizing role there.

The neutral role is still there, i.e. it's still at or near ground
potential.

Now there are some single phase supplies in europe which don't have
a neutral, but they are much less common and only in a few countries
(not UK). An example is a single phase supply from a corner grounded
delta, where both of the lines are taken from a non-grounded corner.

There are also IT supplies which are isolated with just a resistance
to ground to prevent the secondary capacitively floating up to the
much higer primary voltage. Strictly the side with the resistor to
ground is still called a neutral, although it might be some way from
ground potential. Again, I believe some parts of Europe use this,
but it only occurs in the UK on standalone generators, not from the
public supply.

Signature

Andrew Gabriel

phil-news-nospam@ipal.net - 05 Oct 2006 18:45 GMT
In alt.engineering.electrical Andrew Gabriel <andrew@cucumber.demon.co.uk> wrote:
|> In alt.engineering.electrical Andrew Gabriel <andrew@cucumber.demon.co.uk> wrote:
|>|> In Europe, the term "neutral" does include a grounded conductor in a 120 v
[quoted text clipped - 12 lines]
| The neutral role is still there, i.e. it's still at or near ground
| potential.

But that's not what the meaning of neutral is.  It's neutral whether
it is grounded or not.  In cases where there are 2 or mroe phases,
the idea is that when things are in balance, there is no current on
the neutral.  It was neutralized by the balance.  But I think the
meaning really comes from the neutral point in the transformer winding
of the secondary.

| Now there are some single phase supplies in europe which don't have
| a neutral, but they are much less common and only in a few countries
| (not UK). An example is a single phase supply from a corner grounded
| delta, where both of the lines are taken from a non-grounded corner.

Apparently these are older connections.  From what I gather, the first
power in much of Europe in the late 1800's was 220/127 three phase.
It appears that predated Edison supplying light to New York, so it
seems he took the 220 voltage and split it for DC.  He likely also
realized, in all his light bulb work, that a lower voltage worked
better on the filament.  I've heard that the 220/127 can still be
found in some remote locations like way north Norway and rural parts
of Spain.  A friend has reported seeing the remnants of 220/127 wiring
in buildings in Germany predating WW1.

| There are also IT supplies which are isolated with just a resistance
| to ground to prevent the secondary capacitively floating up to the
[quoted text clipped - 3 lines]
| but it only occurs in the UK on standalone generators, not from the
| public supply.

The reason they use that resistance instead of a solid ground is to avoid
single fault failures.  But during that time, one hot line is now grounded.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-10-05-1237@ipal.net |
|------------------------------------/-------------------------------------|
Mark Lloyd - 29 Sep 2006 23:06 GMT
[snip]

>GFCIs (5mA) are now required to not work with reverse load-line terminal
>wiring.

Even when that's exactly what you want.

> (Previously the load terminals connected to the receptacle.) I
>don't think you can do that without double pole contacts line-receptacle
[quoted text clipped - 4 lines]
>In both cases testing can be easily done without a hammer but so far I
>have been too lazy.

[snip]
Signature

87 days until the winter solstice celebration

Mark Lloyd
http://notstupid.laughingsquid.com

"The government of the United States is not, in
any sense, founded on the Christian religion."
-- George Washington

Bud-- - 30 Sep 2006 16:27 GMT
> [snip]
>
>>GFCIs (5mA) are now required to not work with reverse load-line terminal
>>wiring.
>
> Even when that's exactly what you want.

When the supply wires are connected to the LOAD terminals on old GFCIs,
the GFCI receptacle is not protected - it is live even if the GFCI is
tripped. (I believe the downstream circuit, which would be connected to
the LINE terminals, is protected.)

Under the new UL standard, which I think was adopted about 2 years ago,
if you connect supply wires to the LOAD terminals the GFCI receptacle
and LOAD terminals will always be dead.

I may have tried to say that with too few words.

bud--
Mark Lloyd - 30 Sep 2006 18:02 GMT
>> [snip]
>>
[quoted text clipped - 7 lines]
>tripped. (I believe the downstream circuit, which would be connected to
>the LINE terminals, is protected.)

Which is what I wanted. This GFCI is installed inside (where no GFCI
protection is needed) and it controls an outside light. The GFCI acts
as a light switch (at least it used to, before I had to replace it
with one of those "improved" ones).

>Under the new UL standard, which I think was adopted about 2 years ago,
>if you connect supply wires to the LOAD terminals the GFCI receptacle
[quoted text clipped - 3 lines]
>
>bud--
Signature

86 days until the winter solstice celebration

Mark Lloyd
http://notstupid.laughingsquid.com

"The government of the United States is not, in
any sense, founded on the Christian religion."
-- George Washington

phil-news-nospam@ipal.net - 01 Oct 2006 01:19 GMT
In alt.engineering.electrical Bud-- <remove.BudNews@isp.com> wrote:

|> [snip]
|>
[quoted text clipped - 13 lines]
|
| I may have tried to say that with too few words.

Someone once told me that the GFCI receptacles that I found were DANGEROUSLY
susceptible to strong radio fields, must have been wired in reverse.  But I
do know they did cut off the power to its own outlets, so I am convinced
that they were wired correctly.  Maybe they are defective products and the
internal solenoid that trips the mechanism was wired on the LINE side and
should have been wired on the LOAD side.

What happens is that when a strong radio field is introduced, the GFCI sees
this somehow as leakage current.  Other than for it being the wrong frequency
this is understandable, as the induced currents would be in common mode, with
the same direction on hot and neutral.

The DANGEROUS part is that even though the solenoid has opened the circuit
and cut off the power from the outlets (and presumably upstream, which was
not present for the ones I did this with), as long as the radio current was
present, the solenoid continued to activate.  I believe that these solenoids
would be operating from the 120 volts AND are not designed for the heat that
would result from continuous operation.  They would have been designed with
the idea in mind that as soon as the circuit opened, the leakage current
would no longer be present.

This creates TWO hazard conditions.

The first is that if a radio field that caused this was external, it might
not be known to the radio operator that there was a problem.  It could cause
the solenoid to overheat, melt insulation, short circuit, arc, catch fire,
burn the house down, and KILL PEOPLE.  I did NOT leave the radio field on
for a long period of time when I did this test.  Even for the very first
time I discovered this, the loud buzzing of the solenoid in the GFCI was
loud enough to get my quick attention and realize the radio was triggering
the problem.  So I was never doing this for more than a second or two.

The second hazard exists if the GFCI breaker does NOT open the neutral.
A neutral could have some low voltages present as a result of voltage drop
between various L-N 120 volt loads and the point of bonding neutral to
ground.  A short circuit from neutral to ground might not have a great
spectacular arc flash, but it could draw enough current to activate a GFCI
at the 5ma level.  The type of GFCI that allowed the radio current to trip
the solenoid continuously would also result in continuous activation of the
solenoid in this neutral-only leakage situation because the neutral would
not be opened, and the GFCI control circuitry would still be powered.

I believe a proper GFCI design must cut off its own power when tripped, so
it is not doing a continuous trip.  This could be done by powering the GFCI
control circuitry, including the solenoid, from the LOAD side.  When I
suggested this in a posting somewhere a long time ago, someone said that
it may be needed to power the solenoid from the LINE side to ensure that
it completes its operation to full open the contacts.  I can agree that
leaving the contacts stuck in a partial open state where they may arc
across is not a good thing.  But this should be accomplished through the
mechanical energy stored in the unfatiguable spring mechanism that gets
charged when the unit is reset.  The solenoid should just be releasing
that spring.

DO NOT DO THIS AT HOME OR WORK.  There is the risk that some of these units
may be so defective that even a short period of operation could result in
substantial damage.

I also do not know if GFCI breakers have this risk.  If their internal
circuitry remains energized from the bus contacts in the panel, a radio
field could cause the very same problem.  Although they clearly do have
the proper spring loading mechanism, being a part of a circuit breaker,
the solenoid that releases that mechanism when leakage current is detected
would potentially be under continuous operation if the power remains and
the apparent leakage issue remains.  This would not only be a problem
with a continuous radio field, but it could also be a problem when the
neutral has enough voltage to make a leak to ground, such as in a subpanel.
So DO NOT DO THIS NEAR A BREAKER PANEL.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-09-30-1853@ipal.net |
|------------------------------------/-------------------------------------|
Ben Miller - 29 Oct 2006 20:11 GMT
> What happens is that when a strong radio field is introduced, the GFCI
> sees
[quoted text clipped - 3 lines]
> with
> the same direction on hot and neutral.

It is more likely that the rf is getting into the GFCI electronics directly,
rather than through the toroid. I suspect the input to the chip is fairly
high impedance, and there may even be some non-linearity that acts as a
detector.

I know you have mentioned this before, and although I have never experienced
it, I can easily believe that it can happen. I might try some experiments to
replicate it. Do you have any idea of how strong and at what frequency the
rf was?

Ben Miller

Signature

Benjamin D. Miller, PE
B. MILLER ENGINEERING
www.bmillerengineering.com

PPS - 29 Sep 2006 23:17 GMT
> I have been told, but have never sacrificed a device to verify, or set up
> the appropriate test, that GFCI receptacles open BOTH the hot wire AND the
> neutral wire when they trip.  If so, why is that?  Is it to offer at least
> some protection even when the device is miswired?  Or is there even some
> risk with voltages on the neutral wire?

Just opens the ungrounded conductor, not the ground (mistakenly called a
neutral). It uses a special transformer to measure the current on the
grounded and ungounded lines, and if they are not the same (within 5ma) it
trips; assums that the lost current is leaking to ground somewhere (possibly
through a person).

> I do believe some neutral wire risk exists.  It's certainly not as much as

Although the grounded conductor carries the same current as the ungrounded
(white or identified) conductor (a white wire is only a neutral in a 120/240
volt circuit, and carrys the unblanced load of the 120/240 volt applaince),
it's at the same potential as you are. Both are grounded to the earth and
(hopefully) there is no potential difference when a person contacts the
white wire; threrefor no shock hazzard (under normal conditions, IE wired
properly in the first place.)
phil-news-nospam@ipal.net - 30 Sep 2006 13:53 GMT
In alt.engineering.electrical PPS <webmaster@npcc.net> wrote:

|> I have been told, but have never sacrificed a device to verify, or set up
|> the appropriate test, that GFCI receptacles open BOTH the hot wire AND the
[quoted text clipped - 7 lines]
| trips; assums that the lost current is leaking to ground somewhere (possibly
| through a person).

So you are the first to contradict the others and say this?

I know how they work.  The issue is whether the groundED conductor, commonly
known as the neutral, is opened as well.

|> I do believe some neutral wire risk exists.  It's certainly not as much as
|
[quoted text clipped - 5 lines]
| white wire; threrefor no shock hazzard (under normal conditions, IE wired
| properly in the first place.)

Not quite true.  The neutral (I don't know why you are caling it ungrounded)
is NOT at exactly the same potential as ground.  If it were, we'd have never
had to have a separate groundING/EGC wire.  The fact is, the neutral CAN be
at potentials above the earth for various reasons.  In most cases it will
be just a few volts or a fraction of a volt due to voltage drop.  In fault
cases, it can be more serious.  In open neutral cases it can be very serious.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-09-30-0750@ipal.net |
|------------------------------------/-------------------------------------|
ehsjr - 01 Oct 2006 06:13 GMT
>>I have been told, but have never sacrificed a device to verify, or set up
>>the appropriate test, that GFCI receptacles open BOTH the hot wire AND the
[quoted text clipped - 4 lines]
> Just opens the ungrounded conductor, not the ground (mistakenly called a
> neutral).

The grounding conductor is irrelevant to GFCI operation.
Both the neutral and the hot are interrupted when
a GFCI receptacle trips.

It uses a special transformer to measure the current on the
> grounded and ungounded lines, and if they are not the same (within 5ma) it
> trips; assums that the lost current is leaking to ground somewhere (possibly
[quoted text clipped - 5 lines]
> (white or identified) conductor (a white wire is only a neutral in a 120/240
> volt circuit, and carrys the unblanced load of the 120/240 volt applaince),

You have the above mis-identified. The neutral *is*
the groundED conductor. The UNgrounded conductor is
(a.k.a. "hot") NOT the white conductor, unless the
circuit is miswired. The white can be re-identified
as black with black tape or equivalent and then used
as a hot wire.

> it's at the same potential as you are. Both are grounded to the earth and
> (hopefully) there is no potential difference when a person contacts the
> white wire; threrefor no shock hazzard (under normal conditions, IE wired
> properly in the first place.)

The difference is that the neutral (groundED) wire carries
current, under normal circumstances.  The groundING wire
does not.  It takes two faults to shock/hurt/kill you if
you are in contact with the grounding wire; it takes one
fault to shock/hurt/kill you if you are in contact with
the neutral wire.

Ed
phil-news-nospam@ipal.net - 01 Oct 2006 11:18 GMT
In alt.engineering.electrical ehsjr <ehsjr@bellatlantic.net> wrote:
|>>I have been told, but have never sacrificed a device to verify, or set up
|>>the appropriate test, that GFCI receptacles open BOTH the hot wire AND the
[quoted text clipped - 8 lines]
| Both the neutral and the hot are interrupted when
| a GFCI receptacle trips.

So why is the neutral opened?  That's an "academic question" (I can come up
with what I think are good reasons to do so).  Now, considering answers to
this question, what protections might be lost if AFCI breakers that include
GFCI protection at the 5ma level result in GFCI receptacles not being used?
Is GFCI protection in a breaker considered adequate for the requirements in
NEC 210.8 even though it does not open the neutral connection?  Would YOU
persoanlly feel less safe if all the receptacles in a kitchen were protected
for ground fault leakage only by circuit breakers at the panel (assume that
the panel is close by).

There must be _some_ reason _they_ chose to include opening the neutral in
GFCI receptacles (maybe more than one).  But wouldn't such reasons also be
applicable to circuit breaker based protection?

What if you have _both_ GFCI protection at the breaker _and_ GFCI protection
at the receptacle, say in a bathroom.  Now suppose there is a slight leakage
fault, but only the breaker opens on it.  Maybe the receptacle was going to
interrupt the fault, but was just sufficiently slow, perhaps due to a slow
rise in the leakage current, that the breaker did it first, which prevents
the receptacle from doing so.  Now you have a condition where the neutral
continues to be fully connected all the way from the main panel, through
the GFCI receptacle that no longer has power on it's hot wire, and into the
plugged in appliance that someone grabbed with a dripping wet hand while
also grabbing a towel out of the basin water in the sink.

Well, usually, a neutral doesn't have much voltage relative to ground.  But
if there was some kind of open neutral condition also present (now we are at
the level of _two_ existant problems) and a rather unbalanced load between
the two single phase poles (somewhat common), we could be dealing quite many
volts still available through the GFCI receptacle that didn't trip because
it lost power due to the ground fault that was detected by the breaker first.

So my thinking here is, if there is protection to be gained by opening the
neutral at GFCI receptacles, we should _not_ be requiring that AFCI breakers
be of the type that combine GFCI protection.  And perhaps such breakers
should be prohibited for these circuits.

Of course there is also the issue of the inconvenience of going all the way
to the breaker panel to reset a ground fault.  This could be particularly
so for bathrooms (imagine being dripping wet, wearing only a towel, going
out to the garage or down to the basement, standing on a concrete floor,
to reset a breaker).

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-10-01-0450@ipal.net |
|------------------------------------/-------------------------------------|
Member, Takoma Park Volunteer Fire Department - 01 Oct 2006 18:14 GMT
> In alt.engineering.electrical ehsjr <ehsjr@bellatlantic.net> wrote:
> |>>I have been told, but have never sacrificed a device to verify, or set up
[quoted text clipped - 52 lines]
> out to the garage or down to the basement, standing on a concrete floor,
> to reset a breaker).

What makes you so certain that a GFCI circuit breaker does not open the
neutral?  Have you checked with several manufacturers.

One reason why it might be OK for a breaker to leave the neutral alone
is that it is far less likely and in fact rather difficult for a breaker
to be revere wired.  When a breaker type GFCI operates it will nearly
always open the ungrounded conductor.  There are a lot more ways a
receptacle type of GFCI can be supplied with the ungrounded conductor
controlled by the grounded conductor leg of the GFCI mechanism.
Signature

Tom Horne

"This alternating current stuff is just a fad.  It is much too dangerous
for general use."  Thomas Alva Edison

phil-news-nospam@ipal.net - 02 Oct 2006 09:22 GMT
In alt.engineering.electrical Member, Takoma Park Volunteer Fire Department <postmaster@takomaparkfire.org> wrote:

| What makes you so certain that a GFCI circuit breaker does not open the
| neutral?  Have you checked with several manufacturers.

I've looked at the engineering diagrams, cut-aways, and schematics.
There are no contacts for interrupting the neutral wire.

| One reason why it might be OK for a breaker to leave the neutral alone
| is that it is far less likely and in fact rather difficult for a breaker
| to be revere wired.  When a breaker type GFCI operates it will nearly
| always open the ungrounded conductor.  There are a lot more ways a
| receptacle type of GFCI can be supplied with the ungrounded conductor
| controlled by the grounded conductor leg of the GFCI mechanism.

So basically, there is no goal or interest in specifically opening the
neutral.  It's just a case of opening both in situations where either
might be the neutral.

|---------------------------------------/----------------------------------|
| Phil Howard KA9WGN (ka9wgn.ham.org)  /  Do not send to the address below |
| first name lower case at ipal.net   /  spamtrap-2006-10-02-0306@ipal.net |
|------------------------------------/-------------------------------------|
mm - 26 Aug 2006 03:24 GMT
>>the way a GFCI functions, would it trip
>>if a bad connection were made to it ?
[quoted text clipped - 7 lines]
>I don't think so.  Why would the resistance of a bad connection be any
>different from the resistance of a light bulb.

Let me say what I said another way.  GFCI outlets and circuit breakers
measure if there is a difference between the amount of current going
throught the hot wire and though the neutral wire.   If they are the
same, the gfci sees no problem.  Having a loose connection does not
mean that will happen.  Using an appliance that shorts to your body
and from there to some other path than the neutral wire *would* cause
it to trip.

OTOH, if you took two all-metal screwdrivers, one in each hand, and
stuck one into each of the slots in an outlett, even a GFCI outlet,
you could burn your heart to a fine grey ash, and the breaker would
not trip.  Because the same amount of current was going through the
two conductors.

>I wouldn't assume there will be arcing just because a connection isn't
>tight enough.  So I wouldn't assume that even an arc fault circuit
>breaker would be tripped by a loose connection.  Am I right or wrong?
ehsjr - 25 Aug 2006 05:12 GMT
> the way a GFCI functions, would it trip
> if a bad connection were made to it ?
[quoted text clipped - 4 lines]
>  the terminal to warm up - would the
>  GFCI trip ?)

There's all kinds of "bad connections".
If the bad connection resulted in a difference
of 5 mA or more between the current in the neutral
versus the current in the hot wire, the GFCI
would trip.  The example you gave would not cause
the GFCI to trip.

Ed
Zootal - 25 Aug 2006 06:39 GMT
As others have mentioned, a GFCI would probably not trip. They sense current
differences, and usually have current overload sensing in them also. But a
bad connection causing the terminal to warm up would not trip it unless it
got very hot, and even then the results are indeterminate.

> the way a GFCI functions, would it trip
> if a bad connection were made to it ?
[quoted text clipped - 4 lines]
> the terminal to warm up - would the
> GFCI trip ?)
John G - 25 Aug 2006 07:08 GMT
> the way a GFCI functions, would it trip
> if a bad connection were made to it ?
[quoted text clipped - 4 lines]
> the terminal to warm up - would the
> GFCI trip ?)

So far there has been a lot of misinformation in replies to this thread.

Only the smoke will indicate a simple HOT connection.
If there is any arcing a AFCI should detect the fault and disconnect.

Quote

"The “AFCI” is an arc fault circuit interrupter. AFCIs are
newly-developed electrical devices designed to protect against fires
caused by arcing faults in the home electrical wiring."

****

A GFCI will only protect from differences in the current flowing in the
two conductors beyond the GFCI. It will cutoff the current when a very
small current difference, 5 or 30 ma., is detected and should do it
quick enough to save a person from electrocution.

Neither device is intended to protect from voltage spikes and neither
device can detect a simple hot connection.

A hot connection alone will not csause a difference in current between
the 2 legs of the circuit, only a ground fault can cause that and a GFCI
should detect that.
Signature

John G

Wot's Your Real Problem?

 
Sign In
Join
My Latest Posts
My Monitored Threads
My Blog
My Photo Gallery
My Profile
My Homepage

Start New Thread
Enable EMail Alerts
Rate this Thread



©2009 Advenet LLC   Privacy Policy - Terms of Use
This website includes both content owned or controlled by Advenet as well as content owned or controlled by third parties.