Spray Foam Question

Thread view: 
Enable EMail Alerts  Start New Thread
Thread rating: 
Section 31 - 20 Aug 2006 04:28 GMT
If I use spray foam inside my garage do I have to install a vapour
barrier over it like ordinary insulation ?  I'm in Canada, so I have no
clue if the Ontario Building code says that you have to install a
vapour barrier.

Thank you.
Art  Yokell - 20 Aug 2006 06:51 GMT
Sir:

The reason for installing a vapor barrier is not related to code. If you
want your insulation to stay free of moisture and remain an insulation a
vapor barrier should be placed on the warm side of the insulation. If you
are going to use air conditioning the requirement would be to place a vapor
barrier on the walls and ceiling prior to placing the insulation. If you are
planning to heat the area a vapor barrier and a flame barrier should be
placed on the exposed insulation.

> If I use spray foam inside my garage do I have to install a vapour
> barrier over it like ordinary insulation ?  I'm in Canada, so I have no
> clue if the Ontario Building code says that you have to install a
> vapour barrier.
>
> Thank you.
SteveF - 21 Aug 2006 12:15 GMT
> Sir:
>
[quoted text clipped - 5 lines]
> you are planning to heat the area a vapor barrier and a flame barrier
> should be placed on the exposed insulation.

Hate to break it to you but there is obviously a huge difference between
cold storage and residential construction because that is flat out wrong.

Vapor barrier in a house goes on the warm side.  The only place the vapor
barrier goes up before the insulation is in the very far Southern US.  In
Canada it is ALWAYS on the inside under the drywall regardless of air
conditioning.

Closed cell foams, such as Corbond, do not require a vapor barrier.  Open
cell, such as Icynene, do.

Steve.
Murray Peterson - 20 Aug 2006 13:36 GMT
"Section 31" <derek234@gmail.com> wrote in news:1156044487.873034.102800
@i3g2000cwc.googlegroups.com:

> If I use spray foam inside my garage do I have to install a vapour
> barrier over it like ordinary insulation ?

It depends on the type of foam used.  Low density (open cell) foam requires
a vapour barrier.  High density, closed cell foam is completely air tight
and waterproof, so it requires no other vapour barrier.

> I'm in Canada, so I have no
> clue if the Ontario Building code says that you have to install a
> vapour barrier.

I am in Calgary, so I can't help you with Ontario code requirements.  The
companies that do foam insulation will know the local code requirements.

Signature

Murray Peterson

Art  Yokell - 20 Aug 2006 14:06 GMT
Hey Murray:

Let's not lead this man astray. There is no closed cell spray foam. High
density foam is not as high as one would think. It is used for exterior roof
applications to prevent marring from foot traffic. There is no sprayed on
foam insulation that does not require a vapor barrier. I have been in the
Cold Storage Design and Contruction industry for 30 years and stay on top of
my work. Please don't get this man in trouble with poor advice and have him
replacing the insulation in a year or two.
> "Section 31" <derek234@gmail.com> wrote in news:1156044487.873034.102800
> @i3g2000cwc.googlegroups.com:
[quoted text clipped - 13 lines]
> I am in Calgary, so I can't help you with Ontario code requirements.  The
> companies that do foam insulation will know the local code requirements.
rustyjames - 20 Aug 2006 15:35 GMT
> Hey Murray:
>
[quoted text clipped - 7 lines]
> > "Section 31" <derek234@gmail.com> wrote in news:1156044487.873034.102800
> > @i3g2000cwc.googlegroups.com:

Art,

I'm not saying you're wrong about sprayed in foam needing a vapor
barrier, but can you provide some verification? The info I've come
across tends to lead me to believe no vapor barrier is required (even
building codes).  Or, are you referring to specifically cold storage
design?
Murray Peterson - 20 Aug 2006 15:38 GMT
> Let's not lead this man astray. There is no closed cell spray foam.
> High density foam is not as high as one would think. It is used for
[quoted text clipped - 4 lines]
> this man in trouble with poor advice and have him replacing the
> insulation in a year or two.

Strange -- the manufacturers of the foam products are asserting otherwise
(including the ones that insulated the walls of my house).  For example:

http://www.energsmart.com/images/Builder_0306.pdf

page 8-9 indicates that their product meets Canadian building standards for
air infiltration, and no that additional vapour barrier is required.

Signature

Murray Peterson

atufft@sbcglobal.net - 20 Aug 2006 18:45 GMT
The on-line vendor of http://www.tigerfoam.com/ claims their insulation
serves as a vapor barrier and needs no protection from fire.  They also
claim the R-value is superior to standard glass batt insulation, and
that it is non-toxic.  Maybe the cold storage guy should check this out
and reply again...

> > Let's not lead this man astray. There is no closed cell spray foam.
> > High density foam is not as high as one would think. It is used for
[quoted text clipped - 12 lines]
> page 8-9 indicates that their product meets Canadian building standards for
> air infiltration, and no that additional vapour barrier is required.
Art  Yokell - 20 Aug 2006 21:34 GMT
Well, sales literature like this has been around for years. Please note that
none of the testing indicates no vapor barrier only the claims of the
manufacturer. None of the companies mentioned are amongst the major spray
foam suppliers of the world.

I have had the pleasure of either adding refrigeration equipment within a
year of the initial installation or removing and replacing the insulation
that has had moisture driven into it by the difference in vapor pressure
created by the temperature difference. granted this may not be as pronounced
in a residence but the facts are the facts.
> The on-line vendor of http://www.tigerfoam.com/ claims their insulation
> serves as a vapor barrier and needs no protection from fire.  They also
[quoted text clipped - 19 lines]
>> for
>> air infiltration, and no that additional vapour barrier is required.
Murray Peterson - 20 Aug 2006 22:49 GMT
> Well, sales literature like this has been around for years. Please
> note that none of the testing indicates no vapor barrier only the
[quoted text clipped - 6 lines]
> in vapor pressure created by the temperature difference. granted this
> may not be as pronounced in a residence but the facts are the facts.

I think it's a bit more than just sales literature.  My house walls are
insulated with 2-lb SPF, and have no vapour barrier.  Both the foam
contractor and the building inspector believed that this fully met all
Canadian (residential) building code requrements.  I can't speak for
refrigeration facilities -- that's a different kettle of fish entirely.

Signature

Murray Peterson

Art  Yokell - 21 Aug 2006 01:56 GMT
Murray:
I started out in my initial post saying the the vapor barrier has nothing to
do with buidling codes. The fact that your house has no vapor barrier has no
impact on the discussion. It will in my opinion take some time in a home for
this to become noticable. However, you will slowly but surely be paying for
the lack of a vapor barrier in higher heating or cooling bills.

As a final note I checked the Bayer site and found that they are in
agreement with me. Bayer is the world's foremost producer of raw materials
for foam systems and also produces some of the finest systems themselves. I
am done with this nonsense!

>> Well, sales literature like this has been around for years. Please
>> note that none of the testing indicates no vapor barrier only the
[quoted text clipped - 12 lines]
> Canadian (residential) building code requrements.  I can't speak for
> refrigeration facilities -- that's a different kettle of fish entirely.
PPS - 21 Aug 2006 16:35 GMT
> Murray:
> I started out in my initial post saying the the vapor barrier has nothing
> to do with buidling codes. The fact that your house has no vapor barrier
> has no

I don't know what's in the Canadian Building Codes, but it is certainly
required here in the US (by building codes). And my guess is that they are
also required by the CBC as well.

In the 2003 IRC, "Moisture Vapor Retarders" are required by Section 318
except for certain counties in the extreme southern states or where wall
cavities have beed designed to allow for ventialtion of the moisture.
Murray Peterson - 22 Aug 2006 03:28 GMT
> I don't know what's in the Canadian Building Codes, but it is
> certainly required here in the US (by building codes). And my guess is
[quoted text clipped - 4 lines]
> where wall cavities have beed designed to allow for ventialtion of the
> moisture.

Here is the "final word" as given by the Canadian National Research Council
(NRC):

http://irc.nrc-cnrc.gc.ca/pubs/ctus/32_e.html

The report is detailed, but under the right circumstances (>40mm thicjness,
no impermeable barrier on he cold side), they consider closed cell foams to
be acceptable for vapour barrier in residences.

Signature

Murray Peterson

PPS - 24 Aug 2006 00:56 GMT
Interesting read, thanks for posting. Have they adopted this into the NBC?

Anyone have a rough guess as to what the installed price of closed (such as
Corbond) or open (Icynene) cell foam is going for (per sq. ft.)

> Here is the "final word" as given by the Canadian National Research
> Council
[quoted text clipped - 7 lines]
> to
> be acceptable for vapour barrier in residences.
PPS - 28 Aug 2006 22:24 GMT
Murray, you were absolutely correct. Not only does the closed cell not
require a vapor retarder, it should not be used at all, especially on the
exerior side.

> It depends on the type of foam used.  Low density (open cell) foam
> requires
> a vapour barrier.  High density, closed cell foam is completely air tight
> and waterproof, so it requires no other vapour barrier.
PPS - 21 Aug 2006 16:29 GMT
I'm not familure with the Ontario Building code, but it's required everywhere here in the US [using the IRC] (except for certain warm counties in the extreme southern US, and where the cavity has been designed to ventilated to allow for moisture to escape. This would not be desirable in your neck of the woods.)

Keep in mind that the purpose is to prevent moisture-laden air from penetrating the exterior walls and (when it reaches the dew point inside the insulation) condensing into liquid water. (Moisture in air is measured as a pressure, and can (and will) push through any building product to equalize in dryer air. You need to protect not only insulation, but the studs as well. The entire wall needs to be protected.)

You may also run into other minor problems with spray foam, including protecting it from fire with a fire-protective barrier (all codes regulate when & where foam can be used, most either limit the thickness that can be used, and/or require 1/2" gypsum or concrete), and protection from termites (bugs love to burrow through it). The IRC requires a minimum of 6" clearance above ground level.

> If I use spray foam inside my garage do I have to install a vapour
> barrier over it like ordinary insulation ?  I'm in Canada, so I have no
> clue if the Ontario Building code says that you have to install a
> vapour barrier.
>
> Thank you.
 