In a previous post Wayne Whitney wrote...
> A couple questions about the placement of foundation holddowns for use
> with wood structural panel shear wall segments. First, for a 3" wide
[quoted text clipped - 4 lines]
> the threaded rod anchor in the foundation for greater strength at the
> threaded rod/concrete connection.
The placement you suggest is acceptable. You might consider a compromise:
fudge the HD a little closer to the inside edge of the stud, but not all
the way to the center of the concrete below.
> Second, if there is space available on the outside face of the squash
> post (the side not within the shear wall segment), is it OK to install
> the holddown there? It seems desirable from the point of view of
> reducing eccentricity, but perhaps there is some other reason not to
> do this.
Yes. The only "caveat" is that the trimmer studs must be securely
fastened to the full height studs. Another option is to use a through
bolt type HD or use longer SDS screws so that they capture all the framing
at the location in question.

Signature
Bob Morrison, PE, SE
R L Morrison Engineering Co
Structural & Civil Engineering
Poulsbo WA
bob at rlmorrisonengr dot com
Wayne Whitney - 26 Apr 2006 23:20 GMT
> Yes. The only "caveat" is that the trimmer studs must be securely
> fastened to the full height studs. Another option is to use a
> through bolt type HD or use longer SDS screws so that they capture
> all the framing at the location in question.
Right, I hadn't considered this issue because in the locations in
question there are no trimmer studs (the squash post location is
determined by the presence of a larger opening above). I see that if
a trimmer stud is in the load path, then the trimmer stud must be
attached to the squash post (king stud) in a way that is at least as
strong as the holddown.
As to the original question, it's not a problem for a floor-to-floor
tie to be attached to the top of one face of a squash post and a
foundation holddown to be attached to the bottom of the opposite face
of the squash post?
Thanks, Wayne
Bob Morrison - 27 Apr 2006 01:11 GMT
In a previous post Wayne Whitney wrote...
> As to the original question, it's not a problem for a floor-to-floor
> tie to be attached to the top of one face of a squash post and a
> foundation holddown to be attached to the bottom of the opposite face
> of the squash post?
Shouldn't be a problem. that scenario actually has a tendency to minimize
the effect of the load eccentricities.