i need to cut a wasteline to install a PVC "Y" about 3 feet up from the clean out in the basement for an install of a powder room toilet. Do I need to support the stack before I cut it or would the builder (house built 1920's) have installed supports in each floor during construction? I can see a bolt-on support in the attic (a 2 "U" shaped pieces with flanges on each side of the stack bolted together) Also, if there are no other supports would the weight below be too much for a single support to bear?
Thanks
Scot
srasor AT retrieverconstruction DOT com
> i need to cut a wasteline to install a PVC "Y" about 3 feet up from the clean out in the basement for an install of a powder room toilet. Do I need to support the stack before I cut it or would the builder (house built 1920's) have installed supports in each floor during construction? I can see a bolt-on support in the attic (a 2 "U" shaped pieces with flanges on each side of the stack bolted together) Also, if there are no other supports would the weight below be too much for a single support to bear?
>
[quoted text clipped - 3 lines]
>
> srasor AT retrieverconstruction DOT com
The clamp you see in the attic is called a "friction clamp" and serves
the purpose you are asking about. However it isnt safe to assume there
is one at each floor even though that is the normal practice. Caulked
and leaded joints, or no-hub joints will not hold the weight of a stack
hanging below.
If you have no way to visually check if there is a clamp on the floor
directly above where you plan to make the cut you could simply go to the
local plumbing supply, buy a friction clamp, then nail/screw a couple
blockers on either side of the stack to the underside of the floor
joists in the basement. Then affix the friction clamp to the pipe so its
resting on the blockers. Make your cut, insert your y, and remove the
clamp/blockers.
You will be out the cost of the friction clamp (under 20.00 I would
assume) but it would be the safest bet.
Mark